Transformer Forced Air Fans and Short Circuit Values

Status
Not open for further replies.

buddy91082

Electrical
Jan 22, 2009
169
Hi there. When model short circuits for transformers that have fan assited cooling, would i take kva rating at normal rating or at the fan assitsed rating?

Thanks.
b
 
Replies continue below

Recommended for you

For ANSI-rated transformer, the nameplate impedance is based on the lowest self-cooled rating. For IEC transformers, I believe it is based on the highest forced-cooled rating.

The base kVA used for the impedance should be stated on the nameplate.

 