Hi Steven. I have lived through this many times.
I became responsible for the technical aspects of a small isand system with a couple of wye-delta transformer banks.
Our generators could not withstand block loading of the entire system so after an outage at the plant, they would go back on-line one phase at a time.
In the evening we would be running one set. Our very old sets were prone to unexpected stoppages.
I would sit in my room in the dark, waiting for my boys to get another generator started and on-line.
When they connected the first phase, all the lights on that phase would come on. The wye-delta banks would backfeed about 50% voltage to the other two phases and the incandescent lamps would light dim.
When the second phase went in, the lights would jump in brilliance to almost 100% but not quite.
Due to the voltage drop caused by the heavy current in the neutral, and by the regulation of the overloaded wye-delta bank trying to back-feed one phase of the entire system from an open delta source, the voltage would be low.
Then the third phase would be established and all circuits would have full rated voltage.
Aside issue was burned out refrigerators and freezers. During the time that two thirds of the system was on about 50% voltage, all the small refrigeration compressors would stall. They would sit there cooking on about 300% of FLC. Then the voltage would jump up to rated voltage or some high percentage thereof, with the compressor still stalled.
But not to worry, they all have internal over-temperature protection, right.
Yes, but from time to time, the internal protection would not act fast enough and another motor would smoke.
By the way, the boys did the switching with pole top mounted, fused disconnects or cut-outs.
Imagine in the rain and the dark, handling a sagging, telescopic 25 foot hot stick.
Your partner is holding a flashlight.
The system may be at 50% voltage for longer than expected before the operator can get the end of the hot stick disengaged from one cut-out and inserted in the last cut-out.
My hotel room was on the third phase and I am quite familiar with the sequence.
Bill
--------------------
Ohm's law
Not just a good idea;
It's the LAW!