azril83
Electrical
- Aug 23, 2007
- 12
Good Day Friends,
actually i faced same problem same as one of our member here. i was working at CCGT power plant. our generator was from ABB GT13E2. After finished major overhaul for the generator(rated 15.75kV), and during the commisioning of the generator, our generator protection trigger differential protection (87UAT). This happen when we would like to take high load for big motor rated at 6.6kV. We checked CT connection at the UAT, do some calibration to the REG card, and yet still cannot solve the problem. We then checked the commisioning document and noticed that vector unit setting at the REG card have to be changed to Y7. but during the overhaul we never change any setting at the REG set file. Anybody can explain this?
actually i faced same problem same as one of our member here. i was working at CCGT power plant. our generator was from ABB GT13E2. After finished major overhaul for the generator(rated 15.75kV), and during the commisioning of the generator, our generator protection trigger differential protection (87UAT). This happen when we would like to take high load for big motor rated at 6.6kV. We checked CT connection at the UAT, do some calibration to the REG card, and yet still cannot solve the problem. We then checked the commisioning document and noticed that vector unit setting at the REG card have to be changed to Y7. but during the overhaul we never change any setting at the REG set file. Anybody can explain this?