Sungate
Electrical
- Sep 5, 2008
- 6
We have Wind generators connected to 500V/36kv wye/wye step up transformers, grounded on generator side and ungrounded on MV side. Due unbalanced LV side phase-neutral voltages was decided to install additional transformer to compensate harmonics and to balance the voltage. This transformer is 10A, 500v/500v wye grounded/delta shuld be connected by short but oversized cables (250mcm) to withstand fault current is 25ka in generator circuit, protected by line MV fuse.
I am doubt to use these cables for 10A tranny, that connected by 10A/25A breaker to the WTG bus.
Does anyone meet that kind of problem?
I am doubt to use these cables for 10A tranny, that connected by 10A/25A breaker to the WTG bus.
Does anyone meet that kind of problem?