Im relatively new to protective relaying and I am trying to understand existing schemes that our utility uses.
I have a bus that is feeding a transformer with a NC tie breaker on one side and what I'll call an upstream breaker on the other side of the bus. There is differential protection for the bus that gets the Tie, the upstream, and the circuit switcher leading to the transformer.
My question is that if the differential trips, we lockout the bus. Locking out the bus will ask the tie, and the upstream and the circuit switcher to trip to isolate the fault. Should those breakers also be locked out? I'm thinking they only need to be locked out if they fail, in which it would then lock out and ask their upstream breakers to trip.
To me thats the best way to do it, but I have not been in the protection business for that long. Will each utility do it different, or is there a protection bible out there that shows you the standard way of doing things. Thanks for all comments.
I have a bus that is feeding a transformer with a NC tie breaker on one side and what I'll call an upstream breaker on the other side of the bus. There is differential protection for the bus that gets the Tie, the upstream, and the circuit switcher leading to the transformer.
My question is that if the differential trips, we lockout the bus. Locking out the bus will ask the tie, and the upstream and the circuit switcher to trip to isolate the fault. Should those breakers also be locked out? I'm thinking they only need to be locked out if they fail, in which it would then lock out and ask their upstream breakers to trip.
To me thats the best way to do it, but I have not been in the protection business for that long. Will each utility do it different, or is there a protection bible out there that shows you the standard way of doing things. Thanks for all comments.