Got a project constructed under the 1976 UBC that has three stories of wood and steel framing over parking on a sloping lot.
The ceiling GWB is cracking in at least the second story end unit about 4 feet in from the end wall and I see no settlement issues with the foundation - on piling and no cracking. Don't know about the other units... yet.
I am leaning toward long term creep as the floor joists have a 1.5" thick topping spec'd at 9 psf. I am suspicious about the actual density of the topping too which would make matters worse... When coupled with the other framing, the dead load is 20 psf and the dead to total load ratio is 33 percent, exceeding the 22 percent guideline for table use, triggering a special computer analysis according to the November 2000 catalog, the oldest I have available. If you ignore the 22% issue, the joists appear fine for the loading and span seen.
Has anyone experienced similar long term creep issues in similar circumstances?
Mike McCann, PE, SE (WA)
The ceiling GWB is cracking in at least the second story end unit about 4 feet in from the end wall and I see no settlement issues with the foundation - on piling and no cracking. Don't know about the other units... yet.
I am leaning toward long term creep as the floor joists have a 1.5" thick topping spec'd at 9 psf. I am suspicious about the actual density of the topping too which would make matters worse... When coupled with the other framing, the dead load is 20 psf and the dead to total load ratio is 33 percent, exceeding the 22 percent guideline for table use, triggering a special computer analysis according to the November 2000 catalog, the oldest I have available. If you ignore the 22% issue, the joists appear fine for the loading and span seen.
Has anyone experienced similar long term creep issues in similar circumstances?
Mike McCann, PE, SE (WA)