what would be the approximate vetical drop suspended load limit of a 4' span 5/8" standerd threaded rod
 
Replies continue below

Recommended for you

Look in your AISC design manual under Connections. There are load tables for threaded rods.
 
Howee,
The design strength for an A36 5/8 in dia threaded rod (in LRFD) is
PHI*Rn = .75*Fu*Ag
Ag is the gross area (0.31in^2)
Fu is the ultimate strength (58 ksi for A36)
The result is an ultimate load. The elongation is approx. 1/16th of an inch. The design equation can be found on pg 8-89 of AISC's Load and Resistance Factor Design, Vol II.
Hope this helps
 
Members are designed using their yield strength while connections are designed using their ultimate strength. A threaded rod in this application would be considered a member rather than a connection. Yield in a connection is not the most important limit state and is often an advantage because it allows redistribution of load within the connection.
In limit state design the capacity would be:
crf*fy*As
crf=capacity reduction factor(partial safety factor) appropriate to your code.
There was an article on this earlier this year in the e-newsletter Structural Dzine.
 