Bill3752
Chemical
- Jan 24, 2008
- 138
I have done several a bunch of RV calcs recently where thermal relief protection was the controlling case. I would like to get critical feedbackon some assumptions. For simplicity assume a cooling water system. I have been calculating the expansion coeficient using the delta temp/sp vol between operating and max temp.
For the more narrow case of a dead headed pump (i.e. infinite energy input), I have been using the saturation temp at the Ps/P1 to perform the expansion calcs. The essentially means that the motivation results due to the vapor pressure of the water.
However, I would like to test my themodynamic assumption that this relief is at saturation temperature. The only other "process" that I can envision is that liquid expansion would cause pressure to increase, but since this is a non-compressible fluid that would not make total sense.
Please give me your ideas.
For the more narrow case of a dead headed pump (i.e. infinite energy input), I have been using the saturation temp at the Ps/P1 to perform the expansion calcs. The essentially means that the motivation results due to the vapor pressure of the water.
However, I would like to test my themodynamic assumption that this relief is at saturation temperature. The only other "process" that I can envision is that liquid expansion would cause pressure to increase, but since this is a non-compressible fluid that would not make total sense.
Please give me your ideas.