Temporary 480 Volt Service Question

Status
Not open for further replies.

richanton

Electrical
Jul 15, 2002
128
I need to power 2 loads each from a 480 volt 250 amp breaker. The temporary service is coming from outside a bldg. Can I just have a panelboard with nothing but the 2 - 250 amp breakers or do I need to provide a main breaker per NEC in the panelboard as well.
 
Replies continue below

Recommended for you

Review the up to six service disconnects rule in NEC, assuming that this fits the definition of a service.

If setup qualifies as a feeder, it would work too as long as you have a breaker/fuses at the source protecting the 'temp' panel and the feeder.

Rafiq Bulsara
 
Thanks, I wasn't sure if the service rule applied.
 