Have a Rosemount 3144 TT in series with a Rosemount I/P being looped powered from a Fisher Provox AI CL6859 HART smart I/O. When calibrating the loop with a "R" thermocouple simulator and get up over 75% of the range ~ 17ma the reading on Provox goes minus and have to cycle power to the loop to get it reading again. Replace all parts in the loop at least 3 times!
Has anyone seen anything like this? The reason why the I/P is in the loop, still have a pneumatic control panel that still uses 3 to 15 PSI pressure switches for interlocking.
This loop has been functioning for over 9 months without an issue, and calibrated monthly. Found this issue when doing our January monthly calibration.
Thanks
Frank.
Has anyone seen anything like this? The reason why the I/P is in the loop, still have a pneumatic control panel that still uses 3 to 15 PSI pressure switches for interlocking.
This loop has been functioning for over 9 months without an issue, and calibrated monthly. Found this issue when doing our January monthly calibration.