kalluna
Mechanical
- Jun 25, 2009
- 7
What tank roof thickness criteria is used during API 653? From the section in 653 on Suitablity for Service, it sounds as if roof plates corroded to an av thickness less than 0.09 inches in any 100 inch sq area means the plats should be reapiared or replaced. Is this true then whatever the original thickness of roof plates? We had a case where the API reports specified (as it turns out,wrongly!) a t min of 0.163, not 0.09 in. Of course this gave a too-short life remaining. But is 0.09 in thick roof always the determining criteria for repalcement or repair?