miecz
Structural
- Sep 30, 2004
- 1,400
Article 11.1.3.1 of ACI318 and ACI350 give critical section for concrete shear. This issue came up in a recent thread, thread507-244196, where JedClampett pointed out that, for tanks, the critical section for shear according to Article 11.1.3.1 can be taken at a point "d" from the support for exterior loads only.
Jeds remarks appear to be taken from R11.1.3.1, which clearly states that Figure R11.1.3.1(e) is an example of a condition the shear should be taken at the face of the support.
However, I notice that the Example 5.1 of PCA's "Rectangular Concrete Tanks" states that, for a full tank, shear could be checked at a distance "d" from the base.
So, I wonder if Figure R11.1.3.1(e) is not meant to apply to the base of a tank wall. A tank wall typically has a toe outside the wall, and so does not look exactly like Figure R11.1.3.1(e).
Further, this same load condition applies to any cantilever retaining wall. But my concrete text by Wang and Salmon allows shear to be taken at a distance "d" from the base of retaining walls. Can it be that the toe is considered sufficient to induce compression on the face opposite the load? Or can it be that the joint of a tank acts differently than the joint shown in Fig. R11.1.3.1(a)? Notice that Fig. R11.1.3.1(a) has the steel on the opposite face from the load in tension, while, for a wall/base connection, the steel on that face is in compression.
Jeds remarks appear to be taken from R11.1.3.1, which clearly states that Figure R11.1.3.1(e) is an example of a condition the shear should be taken at the face of the support.
However, I notice that the Example 5.1 of PCA's "Rectangular Concrete Tanks" states that, for a full tank, shear could be checked at a distance "d" from the base.
So, I wonder if Figure R11.1.3.1(e) is not meant to apply to the base of a tank wall. A tank wall typically has a toe outside the wall, and so does not look exactly like Figure R11.1.3.1(e).
Further, this same load condition applies to any cantilever retaining wall. But my concrete text by Wang and Salmon allows shear to be taken at a distance "d" from the base of retaining walls. Can it be that the toe is considered sufficient to induce compression on the face opposite the load? Or can it be that the joint of a tank acts differently than the joint shown in Fig. R11.1.3.1(a)? Notice that Fig. R11.1.3.1(a) has the steel on the opposite face from the load in tension, while, for a wall/base connection, the steel on that face is in compression.