Dear Orionga:
You have a problem...
A directly driven 1800 rpm AC generator having two sets of poles per phase will have an output frequency of 60 Hz.
A directly driven 1500 rpm AC generator having two sets of poles per phase will have an output frequency of 50 Hz.
Perhaps you can see why these cannot be synchronized...not to mention you have not stated which nominal frequency of power you desire to generate.
One answer: for 50 Hz, slow down the 1800 rpm machine to 1500 rpm [ I would not recommend speeding up the 1500 rpm machine to 1800 for 60 Hz ].
Another answer: For 50 Hz, on the 1800 RPM engine, insert a 6:5 ratio speed reduction gearbox to lower the speed of its generator to 1500 rpm.
Still another answer: For 60 Hz, on the 1500 RPM engine, insert a 5:6 ratio speed increasing gearbox to raise the speed of its generator to 1800 rpm, provided the generator can handle the increased speed-cubed centrifugal and other stresses.
Re-reading my response, I realize that another perhaps is that perhaps you have not given us enough background for us to fully grasp what it is you are attempting to do and what your problem actually is.
As another participant here has often stated: "Providing more information yields better answers."
CR
"As iron sharpens iron, so one person sharpens another." [Proverbs 27:17, NIV]