Your MSE wall would be reinforced for about 0.7 to 0.8 times the height of the wall - i.e., 5.6 to 6.4 ft (see BS8006). Therefore, the pool would not be within the zone of the reinforced mass and therefore not within the zone of influence of the active earth pressure 'failure plane'. (45 + >30/2 or >=60 from horizontal. The horizontal pressure that civilperson indicated would be an "overturning" pressure against the reinforced mass - but as you don't have soil - only water, for this height of wall, it is basically (not quite true) a wash. Check the global stability of a slip surface going from behind to underneath the wall - if okay, I'd say you would be okay. Of course, your "wall" must satisfy sliding and overturning which, for the mass described above, I see no reason it wouldn't.