rowingengineer
Structural
- Jun 18, 2009
- 2,468
Back ground: A dumb contract decided a flat slab basement suspended slab needed to be saw cut. The saw cuts are on grid, the columns are on grid, the saw cuts are 40-45mm deep. The cover specified for the project was 30mm, thus assuming all the negative moment steel has been cut in one direction, and possibly 50% or more in the other direction. The slab is still fully propped at the moment; total depth of slab is 300mm, size 30m (100’) x 60m (200’).
The slab depth is sized for punching shear. Don’t have enough reo in the slabs to span from column to column without the continuity of the slab over the columns.
Problem: The client wants to keep the slab but isn’t too concerned about deflections for this level. Says he is willing to live with 3-4 time the original predicted deflection.
Possible solutions:
1. Provided carbon fibre strips to the top of the slab to replace the negative reo, as well as installing some shear studs/bolts. I however have concerns about the durability of this solution with regards to the carbon fibre on top of the slab and in such large amounts. Am considering putting it on the underside, but this would mean $$$$$$.
2. Provide a tensioned system to the underside of the slab. However have limited head height thus not very efficient.
So does anyone have any ideas/thoughts?
Arguing with an engineer is like wrestling with a pig in mud. After a while you realize that them like it
The slab depth is sized for punching shear. Don’t have enough reo in the slabs to span from column to column without the continuity of the slab over the columns.
Problem: The client wants to keep the slab but isn’t too concerned about deflections for this level. Says he is willing to live with 3-4 time the original predicted deflection.
Possible solutions:
1. Provided carbon fibre strips to the top of the slab to replace the negative reo, as well as installing some shear studs/bolts. I however have concerns about the durability of this solution with regards to the carbon fibre on top of the slab and in such large amounts. Am considering putting it on the underside, but this would mean $$$$$$.
2. Provide a tensioned system to the underside of the slab. However have limited head height thus not very efficient.
So does anyone have any ideas/thoughts?
Arguing with an engineer is like wrestling with a pig in mud. After a while you realize that them like it