ASTM requires a new test be run for labs testing high-strength concrete in accordance with C617 that shows that 15 cylinders capped with sulfur exhibit strength within 2% of strength of 15 ground cylinders. In lieu of running these tests, the lab may choose to use the manufacturer's test data. However, I have not found a mfg yet that has run this test. Nor have any labs in my area. And my initial test came up 5% short of the ground cylinders.
Now, I am aware that capping with sulfur 7 days prior to testing should increase the strength. But other than that, does anyone have any guidance or knowledge of this testing being run?
Now, I am aware that capping with sulfur 7 days prior to testing should increase the strength. But other than that, does anyone have any guidance or knowledge of this testing being run?