It is a new 250/333/416/450 MVA, 23kV delta - 240 kV Wye Generator Step Up Transformer getting ready to energize.
All looks good except for (TTR) test(s) on one phase. H1: X1-X2.
Tap 1 is 1% low, Tap 2 OK, Tap 3 1% high, 4 1.5-2.5% high and 5 is 2.5% to 3.5% high. Other phases look OK. We have seven different tests counting the factory tests. Five of the results match. The other two indicate the unit is OK. (See chart)
Factory test shows good results: <0.5% on all phases. The manufacturer assembled and tested the unit at site. Their first on site TTR test got the bad readings listed above.
The vendor blamed the temporary power supply, came back with a different test set and got good TTR readings. (We don’t know which test sets were used.)
Not trusting the supplier, our startup crew ran their own test and got the bad readings. Two more tests with different test sets gave similar readings. (Multi-Amp TR800 & Meggar Three Phase 550503).
The vendor still said it's OK, and said we must be having interference issues with site power. (Power is from a 1500 kVA bank. Testing is done when the rest of the site is not working.)
I asked for an applied voltage test. They put 600V 3-phase on H1, H2, H3 and measured the X terminal voltages. Results were a little better but still off by 2.5%. A second test was done using 600/347 volt power connected to H0, H1, H2, H3. Same results: phase B & C good, phase A off by 2.5% on tap 5. Note that the 600V is only 0.25% of rated H1 voltage.
Winding resistance measurements and excitation current measurements all look reasonable. The results compare across the phases.
The vendor is still saying, no problem, go ahead and energize because their factory test and second set of tests show it is OK.
Are we just not doing the tests correctly? (The testing company has many years of HV testing experience. I have a few years of cranking smaller TTR test sets). I figured testing problems would show up on randomn phases with multiple tests.
What might cause the different test sets to give consistent "bad" readings on one phase and "good" on another, but still give one set of good readings with a different test set?
Is this a typical problem with large transformers? Is there something special we should be doing during the test to isolate outside influences? If so, why doesn’t it show up on Phase B & C? Nothing is energized near by.
Does anyone believe the vendor's claim that the voltages will balance out when we put the 240 kV on it?
It is my decision on whether to energize and see what happens. There is enough variation in the test data for me to suspect some testing issues. But the applied voltage test has me worried. It is too simple to goof up much.
Comments?
All looks good except for (TTR) test(s) on one phase. H1: X1-X2.
Tap 1 is 1% low, Tap 2 OK, Tap 3 1% high, 4 1.5-2.5% high and 5 is 2.5% to 3.5% high. Other phases look OK. We have seven different tests counting the factory tests. Five of the results match. The other two indicate the unit is OK. (See chart)
Factory test shows good results: <0.5% on all phases. The manufacturer assembled and tested the unit at site. Their first on site TTR test got the bad readings listed above.
The vendor blamed the temporary power supply, came back with a different test set and got good TTR readings. (We don’t know which test sets were used.)
Not trusting the supplier, our startup crew ran their own test and got the bad readings. Two more tests with different test sets gave similar readings. (Multi-Amp TR800 & Meggar Three Phase 550503).
The vendor still said it's OK, and said we must be having interference issues with site power. (Power is from a 1500 kVA bank. Testing is done when the rest of the site is not working.)
I asked for an applied voltage test. They put 600V 3-phase on H1, H2, H3 and measured the X terminal voltages. Results were a little better but still off by 2.5%. A second test was done using 600/347 volt power connected to H0, H1, H2, H3. Same results: phase B & C good, phase A off by 2.5% on tap 5. Note that the 600V is only 0.25% of rated H1 voltage.
Winding resistance measurements and excitation current measurements all look reasonable. The results compare across the phases.
The vendor is still saying, no problem, go ahead and energize because their factory test and second set of tests show it is OK.
Are we just not doing the tests correctly? (The testing company has many years of HV testing experience. I have a few years of cranking smaller TTR test sets). I figured testing problems would show up on randomn phases with multiple tests.
What might cause the different test sets to give consistent "bad" readings on one phase and "good" on another, but still give one set of good readings with a different test set?
Is this a typical problem with large transformers? Is there something special we should be doing during the test to isolate outside influences? If so, why doesn’t it show up on Phase B & C? Nothing is energized near by.
Does anyone believe the vendor's claim that the voltages will balance out when we put the 240 kV on it?
It is my decision on whether to energize and see what happens. There is enough variation in the test data for me to suspect some testing issues. But the applied voltage test has me worried. It is too simple to goof up much.
Comments?