Jul 6, 2016 #1 skuntz Chemical Joined Mar 16, 2008 Messages 69 Location US We are installing an RO to let down the pressure downstream of a control valve. Since we are only taking a pressure drop and not taking flow measurements, is it necessary to have straight run requirements?
We are installing an RO to let down the pressure downstream of a control valve. Since we are only taking a pressure drop and not taking flow measurements, is it necessary to have straight run requirements?
Jul 6, 2016 #2 pennpiper Mechanical Joined Dec 9, 2005 Messages 1,687 Location US skuntz, No, if you are not measuring then you do not need any straight run. Sometimes its possible to do all the right things and still get bad results Upvote 0 Downvote