RMalaska
Structural
- Jul 31, 2003
- 12
In a large CMU Shearwall Building (100,000 sq ft, 350’x285’), in Seismic Design Category D, if at the center of the building, in one direction, a line of special steel moment frames is added, such that the moment frames will be taking one-half of the building seismic shear (flexible roof diaphragm); what is the drift limit for that moment frame line?
The Building Dept is arguing that the roof as a whole is assigned a single story drift value from Table 12.12-1 of ASCE 7. Since the exterior of the building is masonry cantilever shearwalls, then the story drift for the roof is 0.010*hsx. Since the moment frame is drift controlled, and taking 1/2 of the building shear, I have to do all sorts of difficult gyrations to make the moment frame work at the 0.010 limit.
Is there any published white paper that talks about the combination of these two lateral systems and, similar to section 12.2.3.2, since we can use independent R values for the masonry shearwalls and moment frames and since we have a flexible diaphragm, shouldn’t we also be able to use independent drift limits (as long as the diaphragm deflection will allow it, which it does in this case)?
The Building Dept is arguing that the roof as a whole is assigned a single story drift value from Table 12.12-1 of ASCE 7. Since the exterior of the building is masonry cantilever shearwalls, then the story drift for the roof is 0.010*hsx. Since the moment frame is drift controlled, and taking 1/2 of the building shear, I have to do all sorts of difficult gyrations to make the moment frame work at the 0.010 limit.
Is there any published white paper that talks about the combination of these two lateral systems and, similar to section 12.2.3.2, since we can use independent R values for the masonry shearwalls and moment frames and since we have a flexible diaphragm, shouldn’t we also be able to use independent drift limits (as long as the diaphragm deflection will allow it, which it does in this case)?