reslife
Mechanical
- Nov 6, 2008
- 16
All,
I’m a recent grad in ME, so my experience with real world problems is limited. I have been tasked with analyzing the HVAC of a server room with an area of about 500 sq. ft. and a raised floor. I don’t have any experience with HVAC analysis, but here is my approach:
1. Determine through manufacturing documents the power load in watts of all the equipment: Computers, servers, uninterruptible power supplies (UPS) and anything else using power in the room.
2. Convert each power to Btu/hr if the heat dissipation is not specified in the manufacturing documents.
3. Convert this total Btu/hr into tons of cooling and then look in some catalogs for systems that can handle my cooling ton requirement.
I assume that the power load from the equipment in the room will be the biggest contributor to the heat, and thus the cooling requirement, so I am focusing on that. Please tell me if this is the standard approach for HVAC analysis. Here are some questions that I still have about my approach:
-I feel like I’m not considering scalability in this approach because I’m only considering what equipment is currently going in the room, and not what might be put in there in the future. Should I consider the situation of having the maximum amount of server racks filled with the most power drawing equipment and calculate the cooling required from this?
-The room is lit with fluorescent bulbs. Since this is a smaller room, can I assume that the heat gain from the light is negligible?
-I was told that there wont be any people in this room, so is it safe to assume heat gain from occupancy is negligible, or is there a standard that I should assume a certain amount of people might be present?
-The room is located in the middle of a larger building with other offices/people. Do I have to factor in heat transfer through the walls/ceiling/floor? (Because the server room doesn’t have any walls that are exposed to the outside weather, I was thinking no).
-There are no windows in this room, but I was wondering how important figuring out the heat transfer through the entry door is.
-If I just add up all the power loads and convert this to tons of cooling, I’m not really considering temperatures even though I have a feeling I should. Am I missing something here?
-I feel like I’m forgetting about the “V” in HVAC. How do I determine whether I need to spec for ventilation or not?
I feel like I might be overanalyzing this problem. I know this is a long post full of many questions, but I do appreciate any help or insight any of you can give a young engineer. Thanks!
I’m a recent grad in ME, so my experience with real world problems is limited. I have been tasked with analyzing the HVAC of a server room with an area of about 500 sq. ft. and a raised floor. I don’t have any experience with HVAC analysis, but here is my approach:
1. Determine through manufacturing documents the power load in watts of all the equipment: Computers, servers, uninterruptible power supplies (UPS) and anything else using power in the room.
2. Convert each power to Btu/hr if the heat dissipation is not specified in the manufacturing documents.
3. Convert this total Btu/hr into tons of cooling and then look in some catalogs for systems that can handle my cooling ton requirement.
I assume that the power load from the equipment in the room will be the biggest contributor to the heat, and thus the cooling requirement, so I am focusing on that. Please tell me if this is the standard approach for HVAC analysis. Here are some questions that I still have about my approach:
-I feel like I’m not considering scalability in this approach because I’m only considering what equipment is currently going in the room, and not what might be put in there in the future. Should I consider the situation of having the maximum amount of server racks filled with the most power drawing equipment and calculate the cooling required from this?
-The room is lit with fluorescent bulbs. Since this is a smaller room, can I assume that the heat gain from the light is negligible?
-I was told that there wont be any people in this room, so is it safe to assume heat gain from occupancy is negligible, or is there a standard that I should assume a certain amount of people might be present?
-The room is located in the middle of a larger building with other offices/people. Do I have to factor in heat transfer through the walls/ceiling/floor? (Because the server room doesn’t have any walls that are exposed to the outside weather, I was thinking no).
-There are no windows in this room, but I was wondering how important figuring out the heat transfer through the entry door is.
-If I just add up all the power loads and convert this to tons of cooling, I’m not really considering temperatures even though I have a feeling I should. Am I missing something here?
-I feel like I’m forgetting about the “V” in HVAC. How do I determine whether I need to spec for ventilation or not?
I feel like I might be overanalyzing this problem. I know this is a long post full of many questions, but I do appreciate any help or insight any of you can give a young engineer. Thanks!