Some reference material:
In the 2001 AISI Cold-Formed Steel Specification, NASPEC 2001, we are directed to appendix A for provisions applicable to the USA. On page A3, the appendix for code section A4.1.2 "Load Combinations for ASD", the 1/3 stress increase is apparently eliminated and instead the 0.75 load factor is used, as in the ASCE 7. This section also specifically states: "When evaluating diaphragms using the provisions of Section D5, no decrease in forces is permitted for load combinations including wind or earthquake loads." Section D5 is the section with a table giving the required safety factors and resistance factors for diaphragms.
The Vulcraft steel deck catalog shows in the diaphragm notes, page 67 note 10, that the allowable diaphragm loads have already been increased by 1/3.
Because the AISI spec removed the 1/3 increase for steel diaphragms, and moved the increase to the load side of the equation only for two or more loads, do we have to multiply all of the diaphragm capacities listed in the steel deck catalogs by 0.75? It seems to me that we do.
In the 2001 AISI Cold-Formed Steel Specification, NASPEC 2001, we are directed to appendix A for provisions applicable to the USA. On page A3, the appendix for code section A4.1.2 "Load Combinations for ASD", the 1/3 stress increase is apparently eliminated and instead the 0.75 load factor is used, as in the ASCE 7. This section also specifically states: "When evaluating diaphragms using the provisions of Section D5, no decrease in forces is permitted for load combinations including wind or earthquake loads." Section D5 is the section with a table giving the required safety factors and resistance factors for diaphragms.
The Vulcraft steel deck catalog shows in the diaphragm notes, page 67 note 10, that the allowable diaphragm loads have already been increased by 1/3.
Because the AISI spec removed the 1/3 increase for steel diaphragms, and moved the increase to the load side of the equation only for two or more loads, do we have to multiply all of the diaphragm capacities listed in the steel deck catalogs by 0.75? It seems to me that we do.