I am looking at designing a new beam lintel, 14 feet long, supporting 8" CMU with brick veneer. Attached to the veneer will be a fabric canopy cantilevered from the face of the building. If the beam were to be located concentric on the CMU with a plate supporting the brick, as typically seen, the beam will be torqued quite a bit. Designing the beam under torsion is not an issue. The question is how to support the torsion forces in the supporting masonry wall, which is most likely unreinforced. Does anyone know of a simple solution? Thanks in advance.
 
Replies continue below

Recommended for you

I would suggest placing columns at each end, extending up to the next level.
 
No simple or appropriate way to connect torsionally to unreinforced wall, or to most reinforced walls. Do as jike says, provide a vertical steel mullion at each end as a bending element to develop the torsion.

Not your question, but when you say the fabric canopy is cantilevered from the veneer, that should not be done. Connect it to reinforced blockwork or steel.
 