When starting a "cold" turbine (non-condensing or condensing type), designed for normal operation with superheated steam, there will be condensation which must be removed. As the turbine warms up, condensation will be reduced, and eventually will cease. Therefore, a reliable system for removal of this condensate must be provided for use during start-up.
According to ASME TDP-1-2013 (Prevention of Water Damage to Steam Turbines Used for Electric Power Generation: Fossil-Fueled Plants), steam traps are not a satisfactory means for removing this condensate. According to the ASME document, a “critical” drain must use a power-operated drain valve as the primary means of condensate removal. A steam trap may be used in parallel with a power-operated drain valve. I recommend that you obtain a copy of ASME TDP-1-2013 if you do not already have it. The ASME document covers the entire steam turbine cycle.
For a steam turbine which operates in the superheated region, the turbine manufacturer will recommend closing the power-operated drain valves at a certain load for any drains from the turbine itself. Typically, I would expect closure in the range of 15% to 20% load. However, you should check the manufacturer’s recommendations for your specific application.
If the installation consists of one boiler and one turbine, the boiler may not deliver the design temperature at the turbine inlet during low-load operation. The conditions at the exhaust of your non-condensing turbine should be checked to determine if the exhaust steam will still be superheated under low-load conditions.
Best of luck!