Plugging was fairly common with the "U" frame motors, the predecessors to the "T" frame.
It is putting full reverse current to a forward running motor. Basically a reversing contactor with no time delay between forward and reverse.
There were two main applications; Rapid reversing of equipment and rapid stopping.
For stopping, the motor was energized in reverse and a switch called a "Plugging switch" or a "Zero speed switch" determined the moment that the motor stopped and disconnected the power.
A plugging switch was a zero speed switch with a latch attachment. A zero speed switch was not safe for plugging to a stop. In the event that a stopped motor was rotated backwards, even at a fairly slow speed, the switch may close and energize the motor. For example, if a mechanic were to put a wrench on the motor coupling and turn it fast enough to close the switch, the motor could kick back towards him with full force. A plugging switch was a zero speed switch with a latch that prevented the switch from re-closing once the motor was at rest. I haven't seen a plugging switch for years, but variations of the zero speed switch may still be used for detection of broken belts.
Bottom line, the current when the motor is spinning backwards is about the same as the DOL starting current.
BUT
Do you have capacitors connected to the motor terminals? That can cause issues with a back spinning motor.
Capacitors will allow the back EMF to flow and may allow the buildup of a fairly high voltage. The actual voltage and current comes under the heading of 'It depends". However, the initial current may be in the order of twice the normal starting current.
Bill
--------------------
"Why not the best?"