star/delta o/load

Status
Not open for further replies.

mec1

Mechanical
Jul 25, 2003
5
i have a 3 phase motor pump rated at 17.9A full load do i fit an o/load in the main contactor line and set it at 11A this being 17.9/sqrt3
 
Replies continue below

Recommended for you

Yes, if this is a standard Y/D starter with O/L relay on the load side (in series with motor windings), of the main contactor. In other words if the O/L relay is seeing the phase currents of the delta conection then your statement is true.
 
Regularly on wye-delta starters the full load current of the motor is shared between two contactors ( 1M and 2M), then the thermal units must be sized for 58% of the full load ampere rating of the motor .
 