Discussing motor-winding differential protection, C37.96-88 §2.4.7 states: “These [87] relays detect low-magnitude fault currents during normal loads and do not trip falsely during high-magnitude external faults, or during starting periods. Differential relays cannot detect turn-to-turn faults in the same winding.”
For ground-fault protection, one of the illustrations in C37.96 includes with the 6 CTs and 3 percentage-differential devices, an “87N” directional-overcurrent relay polarized by neutral current or voltage.
I think also that it’s important to note that §3.2 says: “The complete protection scheme must be chosen to achieve optimum service reliability, safety, and protection of equipment at a reasonable cost. It is essential that the operating characteristics of the chosen motor-protection system be coordinated with those of the supply and, if necessary, the process or load involved if selective operation of the protective and control devices is to be achieved.”
That seems to imply that the process loss can potentially be many multiples of the initial motor and associated protective-relay price. On the other hand, these relays must be included in the maintenance routine, so they are not “free” once installed. The driving force may be the cost of lost production for a motor outage, regardless of it’s size.