Stacking MV Insulators

Status
Not open for further replies.

bceng87SS1517

Electrical
Jan 18, 2017
8
Can you stack medium voltage bus support/standoff insulators and get the same voltage rating at the overall height compared to a single insulator at that height. i.e. if I use two 6" insulators instead of a single 12" insulator should the clearance be "derated" at all? Would the BIL be the same?
 
Replies continue below

Recommended for you

What is the target BIL that are you looking for?

The BIL of the assembly of 2 insulators depends on the staking method and the type of insulator. Based on the curve below, there is a good hope that 2-6" insulators could achieve 150 kV BIL that is the rating of one typical 12" insulator.
However, without an actual impulse test, there will be natural uncertainties to warranty the target BIL value.

See the graph below for reference
Insulator_KV_Nominal_vs_BIL_Height_qw6odz.jpg
 