Are sprinklers required?
NFPA 13 (2013), sentence 8.15.7.1 states that "sprinklers shall be installed under exterior projections exceeding 4-ft in width."
Note that NFPA 13 does not consider private balconies to contain storage. NFPA 13 notes "the committee has stated that combustibles, such as patio furniture, which may be wood or plastic and include cushions, are not sufficient to justify sprinkler protection for balconies that would not otherwise require sprinkler protection."