Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sprinkler requirements for a transfer station 1

Status
Not open for further replies.

Haldorson

Mechanical
Joined
Mar 27, 2011
Messages
92
Location
CA

What protection would be required for a transfer station?

The building is noncombustible construction and ceiling height of 30-feet.
 
From NFPA 13 see below key being “shielding of combustibles is extensive”

These fires are very difficult to control and extinguish because the fire is deep seated. As a firefighter I hated these fires, a lot of work to pullout the burning garbage and separate it from the pile. Sprinklers are really just protecting the structure.

5.4.2* Extra Hazard (Group 2). Extra hazard (Group 2) occupancies shall be defined as occupancies or portions of other occupancies with moderate to substantial amounts of flammable or combustible liquids or occupancies where shielding of combustibles is extensive.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top