keenfirengineer
I'm currently designing a dome atrium with a diameter of 100m and the height ranging from 8m up to 24m.
The highest point being at the center of the dome.
The space below is used as circulation space and pop up kiosk.
Based on British Standards, the height limitation for sprinkler provision is up to 17m.
I have referred to NFPA 13 and it does not state any limitation on the height of sprinkler installation.
Thought of using ESFR but there are height limitations prescribed in NFPA, up to 45ft.
Referred to FM 3-26 (Sprinkler for Non-Storage Occupancies) 2014 and found that FM had prescribed the requirement up to 30m that sprinklers are to be provided based K-Factor and stated minimum supply pressure.
Then found out that in FM 3-26 2019, FM had completely revised the data sheet and now sprinkler provisions up to 30m are based on design density and area of coverage. It states a design density of 0.6gpm/ft2 in an area of 1200 sqft. Never seen a requirement of 0.6gpm/ft2 and already guessing that the flow rate is going to be incredibly high.
Next, tried looking for sprinklers that have approvals with K-factors of 25.2 and noticed that all I could find are ESFR sprinklers.
So back to square one.
Any suggestion on references or sprinklers that would be able to serve such heights?
Anyone knows of any similar buildings and its provisions?
Note: Deluge systems were considered but due to the openness of the space, a double knock system would not be practical as there will be overlapping of zone activation. Plus, the tank size would be incredibly large.