Span chart for neutral supported cable

Status
Not open for further replies.

tem1234

Electrical
Jun 13, 2007
192
Hello,

I'm looking for a chart with the maximum distance between 2 pole for neutral supported cable (aerial quadruplex NS75), 3 phase in aluminium + neutral ACSR , 600 volts.

The cond. size is #6 AWG.

A lineman told me approximately 160 ft, but i would like a good reference about it.

Thanks
 
Replies continue below

Recommended for you

The loading (wind, ice, etc.) requirements for your area are going to have a lot of effect on this number. So will the pole class and guying details you use.

The manufacturer should be able to provide you with some tables calculated for typical values of the above parameters.
 