krbernier
Industrial
- May 6, 2009
- 56
I have 2 350 hp 480v motors running vertical turbine pumps.
they are controlled by allen-bradley SMC -FLEX soft starters.
The station has a 1600a main breaker and each soft start is fed by a 600a breaker.
The soft starts were set for a 15 second stop time. When a pump is stopped it decelerates for a period of time and then trips the 1600A main breaker. Allen bradley were called in and ultimately set the stop time to 12 seconds. The motors were stopped a few times that day without problem. Now that we are starting and stopping the pumps daily instead of letting them run for weeks on end our tripping problem has resurfaced.
it would seem that vfds should have been used for this project. i am going to try and adjust the breakers trip setting to allow more time before trip. if that works am i causing the system damage by doing this?
The easy solution is to set the stop time to 0, but the engineer who designed the system was not willing to do that the last time we looked at this issue.
Any input is appreciated. attached is the drive configuration file
they are controlled by allen-bradley SMC -FLEX soft starters.
The station has a 1600a main breaker and each soft start is fed by a 600a breaker.
The soft starts were set for a 15 second stop time. When a pump is stopped it decelerates for a period of time and then trips the 1600A main breaker. Allen bradley were called in and ultimately set the stop time to 12 seconds. The motors were stopped a few times that day without problem. Now that we are starting and stopping the pumps daily instead of letting them run for weeks on end our tripping problem has resurfaced.
it would seem that vfds should have been used for this project. i am going to try and adjust the breakers trip setting to allow more time before trip. if that works am i causing the system damage by doing this?
The easy solution is to set the stop time to 0, but the engineer who designed the system was not willing to do that the last time we looked at this issue.
Any input is appreciated. attached is the drive configuration file