You are approaching the end of the service life of your resins. You should plan on replacing anion resins every 3 years of service, and cation resins every 5-6 years. Unless of course, you are not that concerned about the water quality.
If your service runs have been trending down on a long-term basis, you can blame the resins. If your trending down is a shorter term (weeks), it is probably a different problem.
It is normal that the anion resins exhaust on silica. Anion exchange resins weakly hold silica; therefore, as the exchanger exhausts, silica appears in the effluent well before the ionic contaminants. Silica is poorly ionized and cannot be detected by measuring conductivity; therefore, continuous wet chemical analysis is recommended between the cation and anion beds.
It is normal to have an elevated pH (8-10) after a cation/anion demineralizer. train since the effluent will have traces of NaOH. Na from the cation unit and OH from the anion unit