Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

SLC500 temperature control

Status
Not open for further replies.

KParker150

Mechanical
Oct 7, 2006
1
We want to control temperature with an SLC 5/03 controller and a SLC500 NT4 thermocouple input. Is there any good software available to help with the setup of something like this and a PID loop?
Thanks
 
Replies continue below

Recommended for you

The SLC5/03 is perfectly adequate for PID control on a slow loop such as a temperature controller. What did you mean by software? RSLogix is the native A-B software for the SLC processors and can do what you're asking. A-B's manuals aren't bad to follow. You will need some form of output card from the PLC to control your heat source.

Tuning a temperature loop is either dead simple or a nightmare - the latter usually arises from long transport delays in the process between a controller demand change and the process variable at the sensor responding. Good control using PID in a loop with a long transport delay is tricky - often feed-forward yields better results.

You might want to check out the Ziegler Nichols tuning method if your process is amenable to it. This link gives a fair explanation, and any control engineering text will have this and a lot more detail.



----------------------------------
image.php
Sometimes I only open my mouth to swap feet...
 