mjr6550
Structural
- Jun 27, 2006
- 69
I have a client who is building a one-story dwelling on a site in Philadelphia. Had soil borings performed and soil is generally good, except for about 2 to 4 feet of fill. There had been a structure on the site that was demolished. The 4 feet of fill is in that area. I really will not know the exact extent of fill until we start excavating. The dwelling must be constructed on a slab-on-grade foundation (33x50).
I am looking for some input for options to deal with the fill. Excavate and replace with compacted granular fill; excavate and replace with flowable fill; one-way reinforced slab bearing on intermediate foundation walls; two-way slab on concrete piers; something else? I am planning on extending the foundation walls down to undisturbed soil, so this should not be an issue. The contractor is not experienced at dealing with these issues (no, we can't get another one). I do not have the experience to know which is most cost effective. I'm concerned about the problems the contractor may have with their lack of experience at compacting fill. The city will require testing.
I have a similar project where a homeowner has a family room (13x20) and a garage (20x20) that have settled an excessive amount. There are voids varying from 6 inches to 2 feet below the slab and I can push a 1/2 inch rebar at least 3 feet into the soil (silty clay) with relatively little effort. I'm going to need a similar design to repair this. Any thoughts would be greatly appreciated.
I am looking for some input for options to deal with the fill. Excavate and replace with compacted granular fill; excavate and replace with flowable fill; one-way reinforced slab bearing on intermediate foundation walls; two-way slab on concrete piers; something else? I am planning on extending the foundation walls down to undisturbed soil, so this should not be an issue. The contractor is not experienced at dealing with these issues (no, we can't get another one). I do not have the experience to know which is most cost effective. I'm concerned about the problems the contractor may have with their lack of experience at compacting fill. The city will require testing.
I have a similar project where a homeowner has a family room (13x20) and a garage (20x20) that have settled an excessive amount. There are voids varying from 6 inches to 2 feet below the slab and I can push a 1/2 inch rebar at least 3 feet into the soil (silty clay) with relatively little effort. I'm going to need a similar design to repair this. Any thoughts would be greatly appreciated.