NBRY1...I see you are in Georgia and presumably from your water table question, somewhere in south or coastal Georgia.
A capillary break needs to have a fineness modulus of somewhere above about 2.5. Fine gravel is even better. With that in mind, extend the capillary barrier a few feet beyond the slab on grade and you'll be fine with a shallow water table. I practice in Florida and Georgia and have seen this many times.
If your slab is confined by a footing or stem wall, you obviously can't conveniently extend beyond the slab, so increase the fineness modulus or use fine gravel. If the water table gets to the bottom of the capillary barrier, you'll be ok. If it goes higher, it's no longer a capillary rise issue but a hydrostatic pressure issue.