I have a single story Manufactured container with dimensions of ~60x15. There are no interior shear walls. Seismic controls the design. The container needs fire rating so there is plenty of heavy gypsum on the roof and walls (shear wall is gypsum on cold-formed framing). However, the floor has the majority of the seismic weight because 25% of the floor 500 psf live load is assumed as storage (12.7.2(1)), and an assumed 15% of total container dead load for permanent equipment load.
Questions:
1.) Do I need to distributed the loads vertically per 12.8.3 since this is a single story building on grade? I normally do (perhaps conservatively) by assuming (3) levels: midpoint of floor, midpoint of walls, and midpoint of roof. I have reviewed other engineers' work of single story buildings on grade where the distribution was accomplished by multiplying the weight of each "level" by Cs. Per the P.E. in our office, the distribution of section 12.8.3 is supposed to be done even for single story buildings.
2.) If the building were put on concrete piers, would this change the answer above?
The large mass of the floor is making my shear wall forces unmanageable if vertical distribution is done per section 12.8.3.
Juston Fluckey, E.I.
Engineering Consultant
Questions:
1.) Do I need to distributed the loads vertically per 12.8.3 since this is a single story building on grade? I normally do (perhaps conservatively) by assuming (3) levels: midpoint of floor, midpoint of walls, and midpoint of roof. I have reviewed other engineers' work of single story buildings on grade where the distribution was accomplished by multiplying the weight of each "level" by Cs. Per the P.E. in our office, the distribution of section 12.8.3 is supposed to be done even for single story buildings.
2.) If the building were put on concrete piers, would this change the answer above?
The large mass of the floor is making my shear wall forces unmanageable if vertical distribution is done per section 12.8.3.