I want to perform a single phase test on a 500HP 480VAC 3550RPM twelve tap star/delta motor in order to check the condition of the squirrel cage rotor.
I have a 15KVA three phase delta/delta step down transformer for 480VAC to 240VAC. The delta secondary has a center tap (stinger leg). I intend to excite the primary with 208VAC. I think that the center tapped secondary should provide 52VAC. I would use the 52VAC to excite one winding of the motor. The motor will be disconnected from its normal source of power and I will force the contactors into a star configuration for the test. I will slowly rotate the motor shaft one revolution while monitoring excitation current. If current deviation is less than 5% then my rotor is in good shape. This test will only take app. 30 seconds.
Any problems with this concept?
I have a 15KVA three phase delta/delta step down transformer for 480VAC to 240VAC. The delta secondary has a center tap (stinger leg). I intend to excite the primary with 208VAC. I think that the center tapped secondary should provide 52VAC. I would use the 52VAC to excite one winding of the motor. The motor will be disconnected from its normal source of power and I will force the contactors into a star configuration for the test. I will slowly rotate the motor shaft one revolution while monitoring excitation current. If current deviation is less than 5% then my rotor is in good shape. This test will only take app. 30 seconds.
Any problems with this concept?