I disagree. In a three phase system, unless there is a ground fault, the event that causes one fuse to blow must have occurred in at least two of the phases, but you only see the one. The fuse that cleared was just the first one to go and once it cleared, the current stopped so the other(s) didn't need to clear. But they still saw some if not most of the fault current up to that point and are stressed. That means it might take less current to cause the other fuses to clear next time. That is not inherently dangerous, but it is a nuisance.
If you cut open a good fuse and look at how they are made, you can better appreciate how the near-clear fault current can deform the fuse element and weaken it. Years ago when I started in this industry, we used fuses with replaceable links (now illegal here in the US). My first boss made us replace all 3 links if one blew, and that gave us newbies the opportunity to see the other two "good" fuses. It was an eye opener.