  • Congratulations IRstuff on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!
Simpson Tie Down Values, LRFD
JStructsteel
1,462
So, my wind load is per ASCE 7-10, so Im taking as ultimate load. For connection tie downs, the NDS has a 3.32 conversion factor for the capacity of the connector, and a phi factor 0.65.
Question about Simpson catalog has the capacities with the duration of load at 160%. Do I leave that 160%, and then just increase my capacity of the connector for the 3.32*065?
Always confused about this.
You'd likely need to convert it back to a 1.0 load duration factor. Cd is ASD only.
Curious though. Why? I've never met a US engineer that uses LRFD for wood design.
phamENG, I understand the wind design from ASCE7-10 is a ultimate load now.
That it is...but that's why we have ASD load combinations. 0.6W and all that.
Notice that 7-05 and earlier used 1.6W for LRFD and 1.0W for ASD....7-10 and later use 1.0W for LRFD and 0.6W for ASD.
The difference in the wind speeds is all return period based. So for a RC2 building (like a house), 7-05 and earlier were based on a 50 year MRI and 7-10 and later are based on a 700 year MRI. The 0.6 roughly approximates the 50 year MRI wind load from the 700 year MRI wind load.
PhamENG, gotcha. That makes sense, will use the ASD load combos. Strange the NDS has conversion factors.
Well there is an LRFD procedure for wood...it just isn't widely used in the states. As I understand Canada uses Limit State Design (their version of LRFD) almost exclusively.