fiberstress
Mechanical
- Feb 11, 2009
- 44
Hello,
I have a 480/277V PDU with an onboard transformer that steps down to 208/120V, and then branches into 2 panels (or 3, I’m not sure) supplying 208V L-L/ 120V L-N (3 phase of course).
We need to add two new circuits for two AC units that run on 208V and need 50A breakers each. We're calculating the potential KVA of the panel based on circuit breakers amps and their voltages, which is conservative, but nevertheless my question is for the 2-pole breakers in the panel (20A for example) do we calculate the potential power as follows:
208V x 20A = 4.16KVA ?
And for the 3-pole breakers in the panel (30A for example):
120V x 30A x 3 = 10.8KVA ?
Also, is there a good estimate for the percentage of current breakers typically use? (I've heard 80% is good for calculation purposes)
Thanks for the help.
I have a 480/277V PDU with an onboard transformer that steps down to 208/120V, and then branches into 2 panels (or 3, I’m not sure) supplying 208V L-L/ 120V L-N (3 phase of course).
We need to add two new circuits for two AC units that run on 208V and need 50A breakers each. We're calculating the potential KVA of the panel based on circuit breakers amps and their voltages, which is conservative, but nevertheless my question is for the 2-pole breakers in the panel (20A for example) do we calculate the potential power as follows:
208V x 20A = 4.16KVA ?
And for the 3-pole breakers in the panel (30A for example):
120V x 30A x 3 = 10.8KVA ?
Also, is there a good estimate for the percentage of current breakers typically use? (I've heard 80% is good for calculation purposes)
Thanks for the help.