Fritzfrederix

Chemical
May 28, 2003
63
Hi there

I have a problem with converting an S5 to an S7 -file. A great part of my program is converted correctly, except the command B (bearbeiten), ex. B M 0.0 (bearbeiten M0.0).

does anybody know how I can solve that in S7 ?

Thanks in advance
 
Replies continue below

Recommended for you

Hi Fritzfrederix,

You might want to look to the Siemens Support site (on
Then look for "ID 365590" and click the uppermost item ("Indirect addressing in STEP 7 in comparison to STEP 5").

I think the answer to your question is found here.

Eric
 
Hi Fritzfrederix,

You need indirect addressing using AR-registers in S7.
Try using help, search topic indirect addressing. Some examples are provided there.

Greetings
MerlinTheSorcerer
 