KevinWEvans
Electrical
- May 16, 2008
- 2
We have a 69kV delta / 24.9kV gnd wye substation with a feeder that goes to an island. In the fall of 2008, we installed a 3 MVAR shunt reactor bank to counteract the ~3 MVAR of capacitance from the ~24 miles of submarine cable that feeds the island. This seemed to fix all issues we had.
This last fall, (Oct '09) we had an issue where a 50:5, RF 3.0 CT in the substation failed and fried our entire metering circuit. We replaced everything, but had no idea of the cause. A few months later a VT failed, and we chalked that up to damage sustained from the CT failure. A few days ago, we again had a total CT failure on B phase that again fried the entire metering circuit. We can find no data to suggest what might be the cause of these problems. There was no fault on the feeder, and from everything we can find, the sub was operating in normal conditions, no excessive loading. We have just replaced all of the metering transformers as well as the metering circuit.
It has been brought up that perhaps the reactors might be causing an abnormality. I can't think of any reason that they would since they are in continuous operation and the only time they are de-energized is then there is a recloser operation, in which case the capacitive cable is also dropped. But again, there was no reclosing event when the CT failed.
Any help, insight, or general conjecture on what might be happening would be greatly appreciated!
Thanks,
Kevin
This last fall, (Oct '09) we had an issue where a 50:5, RF 3.0 CT in the substation failed and fried our entire metering circuit. We replaced everything, but had no idea of the cause. A few months later a VT failed, and we chalked that up to damage sustained from the CT failure. A few days ago, we again had a total CT failure on B phase that again fried the entire metering circuit. We can find no data to suggest what might be the cause of these problems. There was no fault on the feeder, and from everything we can find, the sub was operating in normal conditions, no excessive loading. We have just replaced all of the metering transformers as well as the metering circuit.
It has been brought up that perhaps the reactors might be causing an abnormality. I can't think of any reason that they would since they are in continuous operation and the only time they are de-energized is then there is a recloser operation, in which case the capacitive cable is also dropped. But again, there was no reclosing event when the CT failed.
Any help, insight, or general conjecture on what might be happening would be greatly appreciated!
Thanks,
Kevin