pwrengrds
Electrical
- Mar 11, 2002
- 233
I am working on a relay upgrade of an existing switchgear. (CA,USA) The utility comes in at (fused at 80E) 60kV, and feeds the switchgear at 5kV though a 5MVA Y-Y transformer with a NGR on the secondary. The switchgear has 3 breakers feeding the plant load and a 5MVA generator which also has a NGR.
There is a motor operated switch across the transformer secondary NGR which,I believe, closes via a pickup of current at 10 amps through the NGR using an IAC relay (16.5 seconds at 2x).
I am not sure of the size of the transformer NGR, though the one on the generator is 200 amps.
As near as I can tell the XO CT relay is used to protect the NGR in case of a fault on the cables to the bus or a bus fault.
The feeders have ground fault protection and trip at 5-10 amp and a short time dial. The generator is set the same as the relay on the XO of the transformer.
I am hoping for some comments about this and if someone else has seen it before and if its a good idea.
Attached is a one line and the trip circuit for the main breaker and the 89 close relay.
There is a motor operated switch across the transformer secondary NGR which,I believe, closes via a pickup of current at 10 amps through the NGR using an IAC relay (16.5 seconds at 2x).
I am not sure of the size of the transformer NGR, though the one on the generator is 200 amps.
As near as I can tell the XO CT relay is used to protect the NGR in case of a fault on the cables to the bus or a bus fault.
The feeders have ground fault protection and trip at 5-10 amp and a short time dial. The generator is set the same as the relay on the XO of the transformer.
I am hoping for some comments about this and if someone else has seen it before and if its a good idea.
Attached is a one line and the trip circuit for the main breaker and the 89 close relay.