Hey,
I would like to know if there would be any technical problem in protecting a 115 kV short overhead line (around 2 km) with distance relay and over current as back up.
The line is dual circuits between a ring substation and 2 outdoor type SF6 circuit breakers feeding 2 step-down transformers 115kV / 13.8 kV vector group DY1 with 400A NGR. The bus tie on the 115 kV side is normally closed while the bus tie on the 13.8 kV side is normally open.
I know that line differential would be better but this is the design we have and the project would be delayed significantly if we would have to change the scheme to differential. I just would like to know if distance would do? Because some are skeptic that the line is too short to be protected by distance relay.
Thanks
I would like to know if there would be any technical problem in protecting a 115 kV short overhead line (around 2 km) with distance relay and over current as back up.
The line is dual circuits between a ring substation and 2 outdoor type SF6 circuit breakers feeding 2 step-down transformers 115kV / 13.8 kV vector group DY1 with 400A NGR. The bus tie on the 115 kV side is normally closed while the bus tie on the 13.8 kV side is normally open.
I know that line differential would be better but this is the design we have and the project would be delayed significantly if we would have to change the scheme to differential. I just would like to know if distance would do? Because some are skeptic that the line is too short to be protected by distance relay.
Thanks