Short circuit current on the load side of buck-boot transformer (autot

Status
Not open for further replies.

mrcheese

Electrical
Oct 4, 2007
25
I need to calculate the SSC on the Load of an autotransformer.
Any help would be appreciated


Ohm's it not just a good idea, Its the law.
 
Replies continue below

Recommended for you

Hello,

You need to have the following data:

Rated power of the transformer
Rated voltage of the windings
Impedance (Short circuit voltage)

With these values you may get a shortcircuit current value that will give you a "good reference" (infinite bus).

You typically determine the nominal current and divide it by the impedance (in per unit), this will be the shortcircuit current magnitude for a three phase fault.