NEC 2005 Aricle 409 requires SCCR rating label on control panel, so far 31 states have adopted this. I'm doing SCCR calculation on my panel (50 KA SCCR required) and have a very fundamental question:
My panel has 2 transformers: one auxiliary disconnect and one control. The PRIMARY sides of these two transformers are protected by fuses that have SCCR rating of greater than 50 KA (200 KA actually). Now on the SECONDARY sides of these transformers, I DO NOT have to use fuses or circuit breakers that has SCCR rating of 50 KA or greater. Am I right???
Thank you,
My panel has 2 transformers: one auxiliary disconnect and one control. The PRIMARY sides of these two transformers are protected by fuses that have SCCR rating of greater than 50 KA (200 KA actually). Now on the SECONDARY sides of these transformers, I DO NOT have to use fuses or circuit breakers that has SCCR rating of 50 KA or greater. Am I right???