Hello, I've read this old thread about Formwork removal and i'm interested in this topic since i'm designing a composite steel-concrete building for the fabricator/erector and he wants to reduce the shoring removal time.


Someone nicknamed NS4U said that "Modulus gain lags strength gain " and others agreed. My concrete professor at the time said this also, but the brazilian code has a equation to predict the time dependency of the elastic modulus based on CRB-FIP model(1990) that shows that the increase in the elasti codulus is faster than the increase in strength.

I'm attaching the CRB-FIP model relevant part .

Using the equation, at the time that the concret has 75% of strength at 28 days, it has 86,6% of modulus of elasticity at 28 days. Can anyone provide a source which contradicts this.

Thank you.



 
Replies continue below

Recommended for you

As far as I know most of the code relationships between modulus of elasticity, and the concrete strength, are empirically derived with E ~ sqrt(fc`). Naturally this means if you double your fc` you'll have less of an increase in E (fc` from 10 -> 20 results in an increase in E of only 41%)

Early age concrete is different. The empirical relationships dont quite hold and need to be used with extreme caution. That said early age concrete in this context is a day old, and so for the time frames we tend to deal with, the relationships will suffice.

You should check out the ACI-U course on shoring and early concrete behavior. It's something like $30 and well worth it. Here are some slides from the lecture on early age concrete behavior.

Pic1_fqiqw0.jpg


Even the code relationships are not so great even for concrete that has aged some. It's best to use a good deal of caution when relying on them for mission critical elements. The Canadian standard has it written right in the code that the expected range is between 80-120% of that predicted by the equations.

EDIT - Should also be mentioned that the slide below is for relatively high strength concrete. I believe the code equations are better for conventionally ranging mixes (20-40 mPa) but cant access anything to show that right now. Does anyone have a comparison table between prediction / experimental from various code equations for conventional mixes?

Pic3_mqjmdy.jpg
 
Thanks Enable.

I'm thinking about something along 4 to 7 days, so this ACI clause does not apply. Also, the concrete has a conventional strength.

Do you know if the ACI prrdiction of time dependent Modulus of elasticity is similar to the onr of CEB-FIP that i posted?

 