Dear friends.
thanks for your response .I read those articles too.what I want to say is that I have ordered a cable with 31.5 KA short circuit capacity.I had assumed that there would be a 3 phase fault somewhere outside cable so the cable would have to resist the current.but now if I assume that there would be an earth fault in one of the cables(single core ) and also assume that cable shield is bonded at both ends to earth then fault current would be shared in two paths ,one in the shield and the other in the earth .the earth fault current would definitely depends on the current capacity of the shield. my situation is that tenderers have offered different shields say:tape ,wire ,tape and wire and with different capacities ,31.5 KA(shared in shield and armor ),7 KA,and even 630 A.I don't know what to do .do I have to force them to give me a larger shield cross section and with special design ?or 630 A is just enough for me assuming that total earth fault current would be large enough for the relays to operate .it's quite possible that I totaly misunderstood the concept .so please help me.
thank you