Let me start by saying that I am an Electronic Engineer, and whilst I have enjoyed exercising the grey matter perusing my first year thermodynamics books, I have doubts over the voracity of the following logic and assumptions. Hence the post to this forum.
The problem:
I am trying to determine the heat load associated with equipment installed within an airconditioned ISO shelter. I see three main sources of heat: 1. Equipment, 2. Heat transfer from high external ambient temps (30 deg C+) through shelter walls/ceiling/floor, 3. Direct sunlight
on shelter externals. At this stage I do not need to be able to separate out each component.
The system is essentially closed with no significant transfer of air inside to out.
Can I use the rate of change of temperature (With A/C cooling off and fan on only) to determine the heat load?
I have tried some calculations using:
Q=m*c*(Tf-Ts) joules - (1).
m = mass of air (kg) (Actual - 30.3kg)
I calculated mass of air using density of 1.2kg/m3*air volume. Volume of air equals shelter internal volume minus a % (20%) for the physical volume of the installed equipment.
c = Specific Heat of Air 1010 J/Kg.K
Tf(Final) and Ts(Start) in Celsius. (Actual Tf = 23 C, Ts = 20 C)
Now my understanding is that Eq (1) is a measure of the total energy used to change the temp and is not referenced to time.
Using:
Watts = Joules/sec - (2)
I can introduce a time relationship. Here is where I am unsure of my logic.
From (1) I get a figure for Q of 91,815 Joules.
Converting to Watts, I have assumed that it will take 91,815 Watts of power to produce the temperature change in 1 second. Is this correct?
If the time taken for the temp to change is 3 minutes (180 sec) the power required would be:
91815/180 = 510 Watts.
Is this a true, albeit rough, reflection of the overall heat load experienced in the shelter?
Initially, I doubted my logic because anecdotal evidence shows that a temp change of 3 deg C in 3 mins is what the shelter is experiencing during the off cycle of the A/C compressor. The figures I have for equipment heat load alone are significantly higher than 510 watts.
What I have described above relates to heat load. I assume that I could apply the same logic and measure the time taken to decrease the temperature and get an indication of cooling power of the A/C system. Am I correct?
In terms of measurement I intend to measure air temp, using a data logged digital thermometer (1 sec Samples) located at the return vent of the A/C system adjacent to the internal A/C thermostat.
Are there any fundamental problems with my logic?
Thanks in advance.
The problem:
I am trying to determine the heat load associated with equipment installed within an airconditioned ISO shelter. I see three main sources of heat: 1. Equipment, 2. Heat transfer from high external ambient temps (30 deg C+) through shelter walls/ceiling/floor, 3. Direct sunlight
on shelter externals. At this stage I do not need to be able to separate out each component.
The system is essentially closed with no significant transfer of air inside to out.
Can I use the rate of change of temperature (With A/C cooling off and fan on only) to determine the heat load?
I have tried some calculations using:
Q=m*c*(Tf-Ts) joules - (1).
m = mass of air (kg) (Actual - 30.3kg)
I calculated mass of air using density of 1.2kg/m3*air volume. Volume of air equals shelter internal volume minus a % (20%) for the physical volume of the installed equipment.
c = Specific Heat of Air 1010 J/Kg.K
Tf(Final) and Ts(Start) in Celsius. (Actual Tf = 23 C, Ts = 20 C)
Now my understanding is that Eq (1) is a measure of the total energy used to change the temp and is not referenced to time.
Using:
Watts = Joules/sec - (2)
I can introduce a time relationship. Here is where I am unsure of my logic.
From (1) I get a figure for Q of 91,815 Joules.
Converting to Watts, I have assumed that it will take 91,815 Watts of power to produce the temperature change in 1 second. Is this correct?
If the time taken for the temp to change is 3 minutes (180 sec) the power required would be:
91815/180 = 510 Watts.
Is this a true, albeit rough, reflection of the overall heat load experienced in the shelter?
Initially, I doubted my logic because anecdotal evidence shows that a temp change of 3 deg C in 3 mins is what the shelter is experiencing during the off cycle of the A/C compressor. The figures I have for equipment heat load alone are significantly higher than 510 watts.
What I have described above relates to heat load. I assume that I could apply the same logic and measure the time taken to decrease the temperature and get an indication of cooling power of the A/C system. Am I correct?
In terms of measurement I intend to measure air temp, using a data logged digital thermometer (1 sec Samples) located at the return vent of the A/C system adjacent to the internal A/C thermostat.
Are there any fundamental problems with my logic?
Thanks in advance.